Electrical Engineering - Three-Phase Systems in Power Applications - Discussion

Discussion Forum : Three-Phase Systems in Power Applications - General Questions (Q.No. 4)
4.
In a certain three-wire Y-connected generator, the phase voltages are 2 kV. The magnitudes of the line voltages are
2,000 V
6,000 V
666 V
3,464 V
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
32 comments Page 1 of 4.

KARNA said:   9 years ago
In star connection line current = phase current,

Line voltage = 1/3 phase voltage.

And in delta connection line voltage = phase voltage,

Line current = root 3 phase voltage.

So, how is the answer 'd' correct?

By this star connection, the answer is 'c'. It's the right answer.

Chado said:   1 decade ago
In wye connection: Line voltage = square root of 3 multiplied to Phase voltage while Line current = Phase current

In delta connection: Line current = square root of 3 multiplied to Phase current while Line voltage = Phase voltage

Karthi said:   9 years ago
In a three phase system star connection line voltage is root of three. So 2000kv multiply with root of three.

In delta connection: Line current = Square root of 3 multiplied to Phase current while Line voltage = Phase voltage.

Shan said:   1 decade ago
For Y(Star connection): Line Voltage=1.732* phase Voltage
For Delta connection: Line Voltage= Phase Voltage.
Accordingly,
=2000*1.732
=3464.10 volts...

Rajiv gandhi said:   1 decade ago
In a three phase system star connection line voltage is root of three so 2000kv multiply with root of three. It is right answer.

B.Teja Sri said:   9 years ago
In Three phase system star connection vl = root(3)Vph.

Given,

2kv = vph Where root(3) = 1.732.

vl = 2000 * 1.732 =3464.

Himanshu Dakre said:   7 years ago
In star connected systems,
Line voltage is √3 phase voltage .
i.e. = 2000 * √3 .
Hence 3464 is the answer.
(8)

Siddu said:   1 decade ago
In star connection line voltage equal to root 3 times of the phase voltage so answer is 2000*1.732=3464.

Anil said:   1 decade ago
Phase voltage is 2000 volts.

So line voltage mutiply with root3 valu = 1.732.

2000*1.732=3, 464volts.

Saravana said:   1 decade ago
Line voltage = root three times of phase voltage
=1.732*2000
=3,464volts


Post your comments here: