Civil Engineering - Structural Design Specifications - Discussion

Discussion Forum : Structural Design Specifications - Section 1 (Q.No. 33)
33.
The over all depth of a solid slab is 20 cm and effective depth is 15 cm. The horizontal distance between parallel main reinforcement should not be more than
30 cm
40 cm
45 cm
60 cm
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
14 comments Page 1 of 2.

Prasad Mhatre said:   6 years ago
Correct explanation @Barish.

Option A is the answer because if it is mentioned that it is a secondary r/f then the correct answer is 450 but here it is main r/f.
(1)

Naga ase teh moi said:   6 years ago
Not more means maximum value so acc. To IS 456:2000 it is 45cm.
(1)

MJM Gcek said:   4 years ago
Yes, you are correct. Agreed @Dipu.
(1)

Barish Raut said:   10 years ago
The answer is wrong.

As per IS 456-2000 Clause 26.3.3 [b (1)], horizontal distance between parallel main R/f bars must be smaller of the foll:

1. 3 times effective depth i.e. 3 x 15 cm = 45 cm.

2. 30 cm.

So, correct answer is [A] 30 cm.

Chhaya said:   8 years ago
Thanks @Barish Raut.

Ma sohail said:   8 years ago
Yes, you are correct @Barish Raut.

Priyal p said:   8 years ago
No, 45 is right answer. See question is should NOT BE MORE.

Arun Kumar said:   7 years ago
30 cm is correct because we always take smaller value.

Ankit raj said:   7 years ago
45 is correct. I agree with the given answer.

Utsav said:   7 years ago
45 is correct that's why they have mentioned the depth of the slab.