Mechanical Engineering - Heat Transfer, Refrigeration and Air Conditioning - Discussion
Discussion Forum : Heat Transfer, Refrigeration and Air Conditioning - Section 6 (Q.No. 1)
1.
A condenser of refrigeration system rejects heat at the rate of 120 kW, while its compressor consumes a power of 30 kW. The coefficient of performance of the system will be
Discussion:
26 comments Page 3 of 3.
Ajith said:
9 years ago
C.O.P = heat/workdone,
=> 120/30,
=> 4.
=> 120/30,
=> 4.
Jnk said:
9 years ago
cop = ref effect / work done.
= 120 - 30 / 30.
= 3.
= 120 - 30 / 30.
= 3.
Jignesh said:
9 years ago
cop = R.E/WORK = 90/30 = 3.
Ankusb said:
9 years ago
I agree with you @Indra 3 is the correct answer.
Indra bhushan rai said:
1 decade ago
Refrigeration effect = 120-30 = 90.
cop = 90/30 = 3.
cop = 90/30 = 3.
Gaurav said:
1 decade ago
C.O.P = favourable effect/work input = 120/30 = 4.
Here favourable effect is rejection of heat.
Here favourable effect is rejection of heat.
Post your comments here: