A thermometer requires 1 minute to indicate 98% of its final response to a step input. If it is a first order system the time constant is
1 minute
0.5 minute
0.25 minute
0.1 minute
Answer: Option
Explanation:

0.98 = 1 - e-1/T or T = 0.25 minute.