Electrical Engineering - Transformers - Discussion

Discussion Forum : Transformers - General Questions (Q.No. 15)
15.
The primary winding of a power transformer should always be
open
shorted
switched
fused
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
24 comments Page 1 of 3.

DM PANI said:   1 year ago
When the secondary load is overloaded, it draws maximum current in the primary side due to which can damage the primary side as well as appliances. Therefore, primary winding of the power transformer is fused.

Babye Getie said:   5 years ago
The Correct option is D, fused.

When the secondary load is overloaded, it draws maximum current in the primary side due to which damaging the primary side as well as appliances. Therefore primary winding of power transformer is fused. Suppose peak voltage of power source is varying then current will also fluctuate so also to limit the current it is fused.
(5)

Sai said:   6 years ago
But we know that we don't use fuse for power t/f we use circuit breakers (switch).
(1)

Chetan said:   8 years ago
In power transformer primary side low voltage and high current so that's why fuse for protection and fuse is also rating is AMP.

Zahoor khan said:   1 decade ago
The primary side has too many turns so we use low gage wire, therefore, it delicate than secondary as well as costly.

JAIDEEP said:   1 decade ago
@Shamraay, you are right.

Kotireddy said:   1 decade ago
What is the reason for not using the switching method?

Shahir said:   1 decade ago
Whenever the t/f is overloaded the overload current is drawn from the primary side to protect the t/f from this over current fuse is used at the primary side of t/f.

So the given answer is correct.

Hyacinth salim said:   1 decade ago
Fuse required in small primary transformer only upto 11 kv, when we say transformer as a general. The answer shall be closed.

The primary winding shall be closed then only it will work as a transformer and produce flux. SHORTED IS THE ANSWER.

FUSE IN SECONDARY MOSTLY AT 415 V side yes.
(1)

Akhilesh said:   1 decade ago
Fused for protection purpose.


Post your comments here: