What kVA rating is required for a transformer that must handle a maximum load current of 8 A with a secondary voltage of 2 kV?
4 kVA
0.25 kVA
16 kVA
8 kVA
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
121 comments Page 5 of 13.

Raghaba Pradhan said:   1 decade ago
Put the formula and get the answer KVA = VI.

Madhav said:   1 decade ago
It is simple.

p = v*i.
= 8*2.
= 16.

Sankurathri brahmaraju said:   1 decade ago
Hai friends, transformer ratings is always measured in KVA.

kva:v*i - (1000*2*8) - 16000 - 16kva.

Manukumari.m said:   1 decade ago
KVA/KV = I.
KVA/2 = 8.
KVA = 16.

Chandragupt Morya said:   1 decade ago
Hello friend,

You know that,
Output = i*v.

So,

= 8*2.

= 16KVA.

Vijay said:   1 decade ago
Well question itself gives us the secondary voltage as well as load current i.e.,secondary current and we know that kva=current*voltage (either primary or secondary).

2kva*8A = 16kva.

Sudipt jena said:   1 decade ago
Transformer is always rated in kva or mva instead of kilowatt or megawatt because of the absence of power factor unlike the motors. And this kva or mva can be derived by multiplying the system voltage with the current. Here the system voltage is 2000 volts and current is 8 amp.

Akash said:   1 decade ago
KVA = Kilovolt * Ampere.
KVA = 2KV * 8A.
KVA = 16KVA.

Pummy said:   1 decade ago
The rating of transformer is given in KVA because the what type of load will connect with the x"mer is not defined.

Arvind chaudhari said:   1 decade ago
KVA = (V*A)/1000 => (16000/8) => 16.