Electrical Engineering - Transformers - Discussion
Discussion Forum : Transformers - General Questions (Q.No. 1)
1.
What kVA rating is required for a transformer that must handle a maximum load current of 8 A with a secondary voltage of 2 kV?
Discussion:
121 comments Page 1 of 13.
SOULMAKER said:
3 years ago
KVA = A * KV.
= 8 * 2.
KVA = 16.
= 8 * 2.
KVA = 16.
(8)
Nisha Thakur said:
3 years ago
KW = KVA,
P= VI.
KVA rating = 2*8 = 16 KVA.
P= VI.
KVA rating = 2*8 = 16 KVA.
(6)
Sanchayan Singha Roy said:
6 years ago
In the question, it is said that the load current is 8A and the secondary voltage is 2KV.
We know that the kva rating of a transformer remains constant be it in primary side or secondary side.
so,
V1*I1= V2*I2.
V2 = 2KV,
I2 = 8A.
KVA rating = V2*I2.
= 2*8 kVA,
= 16 KVA.
We know that the kva rating of a transformer remains constant be it in primary side or secondary side.
so,
V1*I1= V2*I2.
V2 = 2KV,
I2 = 8A.
KVA rating = V2*I2.
= 2*8 kVA,
= 16 KVA.
(16)
ROOPESH said:
9 years ago
Have any formula for change to kW to ka?
(5)
Abhishek said:
9 years ago
Why transformer's rating is in Kva and not in Kw?
(4)
RANJIT RAI said:
9 years ago
Thanks all for explaining it.
(1)
Ramniwas said:
9 years ago
Thanks to all your explanation.
(1)
Praveen j said:
9 years ago
V2*i2 = kVa.
So,
2* 8= 16 kVa.
Ans:- 16 kVa.
So,
2* 8= 16 kVa.
Ans:- 16 kVa.
(1)
KAVYASHREE G said:
10 years ago
All electrical devices that supply power are usually rated in kVA. This includes transformers, UPS's.
(1)
Meet Vekaria said:
10 years ago
For a 300 MW steam turbine, Generator output is designed 353 MVA and transformer is designed for 370 MVA. Why are generator and transformer rating different?
(3)