1.
What kVA rating is required for a transformer that must handle a maximum load current of 8 A with a secondary voltage of 2 kV?
4 kVA
0.25 kVA
16 kVA
8 kVA
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
121 comments Page 4 of 13.

SARANRAJ R said:   10 years ago
Generally we know that ratings of transformer is denoted as kVA then from the given:

KV = 2.

Amps (A) = 8.

Then, (kVA) = 2*8 = 16 kVA.

A.Harish said:   1 decade ago
Load current means secondary current, already we know secondary voltage.

So output load is i*v=kva
i=8A and v=2KVA
So i*v=16kva.

Jaydeep said:   1 decade ago
How we can calculate if kva is given and we have to find out maximum current rating 2kva transformer find max current rating?

Bijith said:   1 decade ago
There are lot of factors to find a transformer single or three phase,

1. Ratings.
2. No of windings.
3. Size (may be).

Rahul Prajapati said:   1 decade ago
Because all losses ( core losses and copper losses ) are calculated in kva. That is why transformer is rated in kva.

Pummy said:   1 decade ago
The rating of transformer is given in KVA because the what type of load will connect with the x"mer is not defined.

Rabbani said:   1 decade ago
Simple KVA = voltage*current.

So as per the question we know voltage = 2kva and current = 8A.
So 2*8 = 16kva.

Md irshad alam said:   1 decade ago
The rating of transformer is represented in kilo volt so that it is divided by 1000, one kilo means 1000.

Piyush said:   1 decade ago
Because of we find kva that means we have to multiply with current so that.

Ans= 2kv*8 (given) =16kva.

Siva said:   1 decade ago
KVA=V1*I1=V2*I2

KVA=(2000*8)/1000

it is divided by 1000 because it is representing in kva