Electrical Engineering - Transformers - Discussion
Discussion Forum : Transformers - General Questions (Q.No. 1)
1.
What kVA rating is required for a transformer that must handle a maximum load current of 8 A with a secondary voltage of 2 kV?
Discussion:
121 comments Page 3 of 13.
Murali said:
1 decade ago
The output rating of transformer in KVA=v*i
=2000*8
=16000
=16KVA
=2000*8
=16000
=16KVA
Raja said:
1 decade ago
Kva in primary = kva in secondary.
Maximum load = 8A = secondary current.
Secondary voltage = 2KV.
.'.KVA = Secondary current * Secondary voltage.
= 8*2*1000.
= 16Kva.
Maximum load = 8A = secondary current.
Secondary voltage = 2KV.
.'.KVA = Secondary current * Secondary voltage.
= 8*2*1000.
= 16Kva.
Hareesh said:
1 decade ago
p (k.w) = vi* p.f
Here secondary voltage = 2 kv
Total load = 8 amps
power factor =0.9
k.w =kva * p.f
= 2000 * 8 * 0.9/1000=14.4
kva = k.w /pf
=14.4/0.9=16 kva
Here secondary voltage = 2 kv
Total load = 8 amps
power factor =0.9
k.w =kva * p.f
= 2000 * 8 * 0.9/1000=14.4
kva = k.w /pf
=14.4/0.9=16 kva
Sireesha said:
2 decades ago
The transformer KVA rating is found out from the formula
Full load secondary current(I2) = KVA/secondary voltage(V2)
From this formula, KVA =I2*V2 = 8*2 = 16
Full load secondary current(I2) = KVA/secondary voltage(V2)
From this formula, KVA =I2*V2 = 8*2 = 16
Ubaid said:
1 decade ago
Because of two type losses in transformer (Core losses and iron losses. Core losses occur from voltage and iron losses occurred from currant) is T/F rating in KVA.
Rahul kumar said:
1 decade ago
The given power is reactive power so how can we say it is a load,
Because reactive power did not require for a load but it work only with inductor and capacitor.
Because reactive power did not require for a load but it work only with inductor and capacitor.
R.ASHOK said:
2 decades ago
Mr.sarbojit 1000 is dividing because we are taking the data as volts not in kv so after getting result we should convert into kv because there given only in kv.
Meet Vekaria said:
10 years ago
For a 300 MW steam turbine, Generator output is designed 353 MVA and transformer is designed for 370 MVA. Why are generator and transformer rating different?
(3)
Md sultan rashid said:
1 decade ago
Isolation transformer is a transformer, which is used for transfer electrical power from a source of alternating current power to some equipment or device.
Omardayah said:
1 decade ago
We know that transformer has voltage and ampere.
So we have to multiply volt and amp 2V and 8A is 16's term of KVA is a unit of transformer.
So we have to multiply volt and amp 2V and 8A is 16's term of KVA is a unit of transformer.