The turns ratio required to match an 80 source to a 320 load is
80
20
4
2
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
101 comments Page 6 of 11.

Engr. Mamoona Akbar said:   1 decade ago
Turn ratio*2 = load impedance/source impedance.

Ranjeet singh said:   1 decade ago
v2/v1 = i1/i2.

= v1/r1*r2/v2.

(v2/v1)^2 = r2/r1.

(k)^2 = r2/r1.

k^2 = 320/80.

k^2 = 4 .

k = 2.

Ramm said:   1 decade ago
Transformer rating is KVA, because iron&Cu losses depending upon the voltage and current only. Then not depending in the pf so its calls kva only.

Gursewak Singh said:   1 decade ago
Turns Ratio = sqrt(r2/r1).
= sqrt (320/80).
= sqrt (4).
= 2.

Prakash said:   1 decade ago
What is turns ratio? please explain.

Arun Kumar Raju C said:   1 decade ago
The turns ratio of a transformer is defined as the number of turns on its secondary divided by the number of turns on its primary.

Akash.bhure said:   1 decade ago
Source resistance(R1) = 80 ohms.

Load resistance(R2) = 320 ohms.

R1 = R2/K^2.
80 = 320/K^2.
K^2 = 320/80 = 4.
K = sqrt(4) = 2.

Saranya said:   1 decade ago
Single phase transformer 50hz 200 kva 11kv/230v test results: no load test: input = 1600watts short circuit test : 2600 watts calculate all day efficiency duty cycle 160kw 0.8 pf 8 hr 100kw unity pf 6hr remaining hrs no load.

Krishnakant said:   1 decade ago
Numerical solution of single and three phase transformer.

Krishna said:   1 decade ago
What is the relation the number of turns and the resistance?