3.
The gap between web plates and flange plates for fillet welds should not be more than
0.5 mm
0.75 mm
1.0 mm
1.25 mm
1.5 mm
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
8 comments Page 1 of 1.

Shivam said:   1 decade ago
As per is 800, clause 8.6.3.5 Welded construction.

The gap between the web plates and flange plates shall be kept to a minimum and for fillet welds shall not exceed 1 mm at any point before welding.
(1)

Agha Bilal said:   2 years ago
As per IS 800-2007 Clause 8.6.3.5, it states;
The gap between the web plates and flange plates shall be kept to a minimum and for fillet welds shall not exceed 1 mm at any point before welding.

So, option C is correct.
(1)

Satya said:   10 years ago
For fillet welds, gap shall not exceed 1 mm at any point before welding.

Thehri said:   10 years ago
Anyone explain the reason.

Roy said:   9 years ago
Yes, it's 1 mm.

Rohit said:   8 years ago
1 mm is correct. Very Good explanation, Thanks @Shivam.

Unique said:   7 years ago
Yes, 1mm is the correct option as per IS800-2007.

Haris said:   7 years ago
1.5 is correct. Agree with the given answer.