Swagatika said:   7 years ago
As per IS 456-2000, this is the case of severe exposure condition and for sever exposure condition nominal cover is not less than 45mm. Ref-(Table-3 & Table-16). The nominal cover size may be reduced 5mm for M35 or above concrete grade. So, the answer 'D' may be correct.

Sourav said:   6 years ago
According to IS 456:2000 Table 16;

For mild condition, cover should not be less than 20mm and for severe condition(totally immersed in sea water) cover should not be less than 45mm.
So, addition cover in this condition should be 45-20mm=25mm.

Sonu said:   4 years ago
The Right answer is 25mm because he said additional not nominal cover/
For the nominal cover, the answer is 45mm.
But for additional cover (45mm - 20mm = 25mm).

Shubham Gupta said:   4 years ago
25 is the right answer because in this question additional cover were asked not nominal cover.
(3)

Prasanna Gosavi said:   5 years ago
Yes, you're totally Correct @Sourav.

So, the correct answer for this question must be 25 mm.

SURAJ PRASAD KESHARI said:   5 years ago
40 is right because,
Additional cover =45 - 20 = 25.
Nominal cover =45 - 5 = 40.
(5)

Barish Raut said:   1 decade ago
As per IS 456-2000 (Table 3 & Table 16) - 50 mm cover.

Deependra pathak said:   7 years ago
45 mm but the most probable answer is 40mm.

Aman Mahadeo Nandeshwar said:   5 years ago
Yes, I also agree with you, Thanks @Sourav.

SURAJ PRASAD KESHARI said:   5 years ago
Yes, you are right, Thanks @Sourav.