Civil Engineering - Soil Mechanics and Foundation Engineering - Discussion

Discussion Forum : Soil Mechanics and Foundation Engineering - Section 3 (Q.No. 19)
19.
A soil sample has passing 0.075 mm sieve = 60% liquid limit = 65% and plastic limit = 40%. The group index of the soil, is
5
20
40
none of these.
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
48 comments Page 1 of 5.

Mukesh joshi said:   6 years ago
A is the correct answer guys.

0.2a+0.01ad+0.005ac.

a = %particle passing through 75micron sieve and their given % should be lie between (35<a>75) means whose value ranges from (0-40) in this question given value is 60% which means (a=60-35=25).

b=%particle passing through 75-micron sieve and lies between (15<b>55) which means (0-40) but in this question which is 60 % so it is not full fill our condition so b=0.

c = liquid limit lies between (40<c>60) which lies on range (0-20) in this question which is 65% so,

c = 0
d = plasticity index lies between (10<d>30) on range (0-20) in this question which is P.I = 65-40=25.

So, its range is d = 25 - 10 = 15.
d = 15.

Summary
a=25
b=0
c=0
d=15

G.I = 0.2a + 0.01bd + 0.005ac.
= 0.2 * 25+0.01 * 0 * 15 + 0.005 * 25 * 0.
= 5.0 + 0 + 0
G.I = 5.0.
So, A is the correct answer.

B.Singh said:   5 years ago
GI= { 0. 2 a + 0. 005 ac + 0. 01 bd } ------> eq. (1).

A = % of soil passing through 0. 075 sieve - 35. {limit 1 < a < 40}.
A = 60 - 35 = 25 (ok within limit).

B = % of soil passing through 0. 075 sieve - 15. {limit 1 < b < 40}.
B = 60 - 15 = 45 (It's over limit) so we will take = 40.

C = Liquid limit - 40. {limit 1 < c < 20}.
C = 65 - 40 = 25 (It's over limit) so we will take = 20.

D = plasticity index - 10. {limit 1 < d < 20}.
{Plasticity index = Liquid limit - Plastic limit}.
D = (65 - 40) - 10 = 15 (ok within limit).

Putting the value of a, b, c, d in eq. (1).

GI = 0. 2 a + 0. 005 ac + 0. 01 bd.
GI = (0. 2 x 25) + (0. 005 x 25 x 20) + (0. 01 x 40 x 15).
GI = 13. 5.
So, The answer will be 13. 5.
And None of these is the correct one.
(13)

Gaurav sharma said:   6 years ago
GI = .2 * a +.005* a*c +.01*b*d.

a = P (% passing from 75-micron sieve ) - 40 (value not more than 40.. if more than 40 then take 40).

a= 60-35= 25 ok not more than 40.
b= P (% passing from 75 micron sieve ) - 15 (value not more than 40.. if more than 40 then take 40),
b= 60 - 15 =45 ( not ok ) (take 40).

c= wL (liquid limit ) -40 (value not more than 20.. if more than 20 then take 20),
c= 65- 40 = 25 (not ok ) ( take 20).

d= IP ( plasiticity index ) - 10,
d=( WL liquid limit( 65) - (40)WP plastic limit )- 10,
= 25-10 = 15 ok value less than 20.

So , G.I = .2*25 +.005*25 * 25 + .01*40 * 15,
and 14.125 is the correct answer.

ARNAB KUMAR BARIK said:   7 years ago
Given:- % passing (P) =60%, LL = 65%, PL = 40%.

We have GI = 0.2a+0.005ac+0.01bd.

To get a,b,c and d value, we need Percentage passing 75 micron IS sieve, Liquid Limit and Plasticity Index.

So Plasticity index = LL - PL = 65-40= 25.
Now a= 60-35=25 (value is 0-40),
b =60-15 =45 (value >40, so take 40),
c= 65-40=25 (value > 20, so take 20),
d = 25-10=15 (value between 0 to 20),
Now GI= 0.2 x 25 + 0.005 x 25 x 20 + 0.01 x 40 x 15 = 13.5.

So the answer is D.

Akash D Sajjanar said:   9 years ago
GI= 0.2a+0.005ac+0.01bd.

a= % passing 0.075 mm sieve (min 35 max 75)= 60-35= 25 (max value is 40 if >40 take a value as 40).
b= % passing 0.075 mm sieve (min 15 max 55)= 60-15= 45 > 40 so take b=40.
c= liquid limit max 40 = 65-40 = 25 > 20 so take c=20.
d= plasticity index = 25-10 = 15 < 20 so d=15.
GI = (0.2*25)+(0.005*25*25)+(.01*40*15)=14.125.

So, answer is GI=14.125.

Arjun said:   6 years ago
G.I = 0.2 * a +0.005 * a * c+ 0.01 * b * d.
G.I = 0.2 * 25 + 0.005 * 25 * 15 + 0.01 * 40 * 10 = 10.875.

a = P-35 = 60 - 35 = 25 ( 0-40 ) Hence adopt this value.
b = P- 15 = 60 - 15 = 45 (0-40) Hence adopt 40 .
c = LL- 40 = 65 - 40 = 15 (0-20 ) Hence adopt this value
d = PI - 10 = 65 - 40 - 10 = 15 (0-10) Hence adopt 10.

Pkota said:   6 years ago
GI = 0.2a + 0.005ac + 0.01bd.
a = F-35 = 60-35 = 25.

Which is less than 40 so a=25
b = F-15=60-15 = 45 which is greater than 40 so take b=40
c = LL-40=65-40 = 25 which must not be greater than 20 so take c=20
d = Ip-10=(LL-PL)-10 = (65-40)-10=15
GI = 0.2*25 + 0.005*25*20 + 0.01*40*15,
= 5 + 2.5 + 6 = 13.5.

Dhruba said:   6 years ago
The answer will be 14.875..so, The option none of these is the correct one.

GI= 0.2a+0.005ac+0.01bd.
a= % of soil passing through 0.075 sieve - 35.
b= % of soil passing through 0.075 sieve - 15.
c= Liquid limit - 40,
d= plasticity index - 10,
Plasticity index= Liquid limit - Plastic limit.

SAMKIT said:   10 years ago
The correct method is;

A = p-35 shud not be greater than 40,
B = p-15 shud not be greater than 40,
C = LL-40 shud not be greater than 20,
D = Ip-10 shud not be greater than 20,

Put in GI = 0.2a + 0.01bd + 0.005ac.
We get GI = 0.2*25+0.01 * 40 * 15 + 0.005 * 25 * 25.
= 14.125.

Pritam yadav said:   7 years ago
a = (60-35) = 25
b = (60-15) = 45 is not more than 40 so let b = 40.
c = (65-40) = 25 is not more than 20 so let c = 20.
d= (60-15) = 45 is not more than 40 so let d = 40.

Calc.,
G.I = (0.2x25)+(0.005x25x20)+(0.01x40x20)
= 15.5.

15.5 will be the correct answer.


Post your comments here:

Your comments will be displayed after verification.