Rakesh Joshi said:   2 years ago
It's based on IS3414:1968 (Reaffirmed 2000).

Clause 3 Installation of Expansion Joint in Walls.

Sub Clause 6.3.1 In brick or stone masonry expansion joints normally need not be necessary, except in the case of long walls exceeding 30 m in length; in such long walls, the expansion joints shall be not less than 15 mm wide and shall be spaced not more than 30 m apart.

Sovan said:   10 years ago
According to IS 3414: 1968.
Cl no. 6.3.1.

In brick or stone masonry expansion joints normally need not be necessary, except in the case of long walls exceeding 30 m in length; in such long walls the expansion joints shall be not less than 15 mm wide and shall be spaced not more than 30 m apart.

Mahendiran said:   10 years ago
In brick masonry or stone masonry, it is provided at the expansion joint of 25M to 30M. It is the correct expansion space at a longer wall.
(1)

Madhusudan said:   1 decade ago
It is not 40 m i.e. 45 m. When the length is more than 45 m we provide an expansion joint for safety.

Manoj said:   10 years ago
Not in 40m, it is provided just 25 to 30 m length when the length of masnory work is more than 100m.

Gaurav said:   6 years ago
According to Clause 6.3.1, IS Code:3414-1968.

30 m will be the answer.
(1)

Prince said:   3 years ago
Why it should be 40m why not 40mm? Anyone, Please explain me.

Chandan Kumar said:   9 years ago
Always in brick masonary and stone masonary is provide 30m.

Rajn said:   5 years ago
30 for masonry and 45 for RCC.
(1)

Bibek Yadav said:   4 years ago
For masonry 40m.

For Rcc 45m.
(2)