Mechanical Engineering - Heat Transfer, Refrigeration and Air Conditioning - Discussion

Discussion Forum : Heat Transfer, Refrigeration and Air Conditioning - Section 4 (Q.No. 16)
16.
The operating temperature of a cold storage is - 2° C. The heat leakage from the surrounding is 30 kW for the ambient temperature of 40° C. The actual C.O.P. of refrigeration plant used is one fourth that of ideal plant working between the same temperatures. The power required to drive the plant is
1.86 kW
3.72 kW
7.44 kW
18.6 kW
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
8 comments Page 1 of 1.

Subhankar said:   7 years ago
@Patel Harshad.

The answer is 13.

AMR said:   8 years ago
Wkt, Ideal COP= Low Temp/(High Temp-Low Temp)= 271/42=6.45;
Actual COP= Refrigerating Effect/Work (or Power) Input =(1/4)*6.45=1.6125
So, 1.6125= 30/Work (or Power) Input (or) Work (or Power) Input=18.6 kW.

Here Actual COP of 1.6125 indicates that 18.6 kW of power input is needed for a evaporator to extract 30 kW of heat from the refrigerated space.

(Notes: Refrigerating Effect means " the quantity of heat that each kg of refrigerant absorbs from the refrigerated space to produce useful cooling". So, Refrigerating Effect=Heat Extracted)

Patel harshad . v. said:   8 years ago
A cold storage is to be maintained at -5*c while the surroundings are at 35*c. that heat leakage from the surroundings into the cold storage is estimated to be 29 kw.

The actual c.o.p of the refrigeration plant is one-third of an ideal plant working between the same temperatures. Find the power required to run the plant.

B.D. BHARAI said:   9 years ago
Here T1 = 273 - 2 = 271 and T2 = 273 + 40 = 313
So, COP = T1/T2 - T1 = 6.45
NOW actual cop is 1/4 of ideal cop
So,
ACTUAL COP = 1/4 * 6.45 = 1.6
basically COP = heat extracted/w.d.
So, POWER = 30/1.6 = 18.6 answer.
(1)

Heisenberg said:   9 years ago
@Mohamme Thank you so much.

Vatsal said:   9 years ago
Thanks, @Mohamme Riyas.

Mohamme Riyas M said:   10 years ago
@Mohit : We know COP = TEMP OF COLD BODY/TEMP OF HOT BODY - TEMP OF COLD BODY.

So here COP = 271/(313-271) = 6.45.

Actual COP = 1/4th of Ideal COP = 1/4(6.45) = 1.6125.

We also know actual COP = Heat extracted/Work input.

1.6125 = 30/WI.

Therefore Power = 30/1.6125 = 18.6 Kw.

Mohit said:   1 decade ago
What is the solution?