1.
What kVA rating is required for a transformer that must handle a maximum load current of 8 A with a secondary voltage of 2 kV?
4 kVA
0.25 kVA
16 kVA
8 kVA
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
121 comments Page 5 of 13.

Hareesh said:   1 decade ago
p (k.w) = vi* p.f

Here secondary voltage = 2 kv

Total load = 8 amps
power factor =0.9

k.w =kva * p.f
= 2000 * 8 * 0.9/1000=14.4

kva = k.w /pf
=14.4/0.9=16 kva

Priya said:   1 decade ago
Q=v*i*10^-3
Q=20000*8*10^-3
Q=16kva

P.H.Hussain said:   1 decade ago
We know that,
Power P=voltage*current
P=2*8=16kw (or) 16kVA.

Virendra mandloi said:   1 decade ago
Why we note transformer's power in kva or mva? but why we do not in khva or mhva?

Bhushan Kumbhalkar said:   1 decade ago
KVA=V1*i1=V2*i2.

Therefore here, V2=2KV, i2=8Amp.

Then, KVA=V2*i2.

KVA=2*8;

KVA=16.

Mohd tajammul akhter said:   1 decade ago
The transformer rating in kva when 2kv is multiplied by 8a then it become 16kva.

L P RAI said:   1 decade ago
We know
E2/E1=N2/N1=I1/I2
>E2/E1= I1/I2
>E1*I1=E2*I2
=2Kv *8A
=16 KVA

We should note (in this question) the rating of transformer meanse input kva rating the out put voltage and current i.e load current is already given.

Kedar apkar said:   1 decade ago
p=vicosQ for single phase p= root3*VICosQ for three phase
Consider 0.95 PF For transformer
0.80 PF for generator
p=2000*8*0.95
= 15200=15.2KW
So PF = KW/KVA we need KVA rating
KVA= KW/PF
= 15.2/0.95=16KVA.

Siri said:   1 decade ago
Here how we can assume power-factor values?

MOHAMED MANSOOR said:   1 decade ago
V2*I2=2*8=16.
Here load current=I2=8A


Post your comments here:

Your comments will be displayed after verification.