Discussion Forum : Transformers - General Questions (Q.No. 1)
1.
What kVA rating is required for a transformer that must handle a maximum load current of 8 A with a secondary voltage of 2 kV?
4 kVA
0.25 kVA
16 kVA
8 kVA
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
121 comments Page 12 of 13.

UJJAWAL PATLE said:   9 years ago
v * A = 2000 * 8\1000 = 16kva.

Meet Vekaria said:   9 years ago
For a 300 MW steam turbine, Generator output is designed 353 MVA and transformer is designed for 370 MVA. Why are generator and transformer rating different?
(3)

KAVYASHREE G said:   8 years ago
All electrical devices that supply power are usually rated in kVA. This includes transformers, UPS's.
(1)

Praveen j said:   8 years ago
V2*i2 = kVa.
So,
2* 8= 16 kVa.
Ans:- 16 kVa.
(1)

Ramniwas said:   8 years ago
Thanks to all your explanation.
(1)

RANJIT RAI said:   8 years ago
Thanks all for explaining it.
(1)

Abhishek said:   8 years ago
Why transformer's rating is in Kva and not in Kw?
(4)

ROOPESH said:   7 years ago
Have any formula for change to kW to ka?
(5)

Sanchayan Singha Roy said:   5 years ago
In the question, it is said that the load current is 8A and the secondary voltage is 2KV.

We know that the kva rating of a transformer remains constant be it in primary side or secondary side.
so,

V1*I1= V2*I2.
V2 = 2KV,
I2 = 8A.


KVA rating = V2*I2.
= 2*8 kVA,
= 16 KVA.
(11)

Nisha Thakur said:   2 years ago
KW = KVA,
P= VI.
KVA rating = 2*8 = 16 KVA.
(3)