According to IS : 800 - 71, the minimum thickness of a vertically stiffened web plate, shall not be less than
none of these.
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
31 comments Page 1 of 4.

Pankaj said:   6 years ago
B is correct.

No stiffeners are provided if the web is more than d/85.

Vertical stiffeners are provided if the web is less than d/85 but more than d/200.

Vertical +1horizontal stiffeners are provided if the web is more than d/200 but less than d/250 (in this case this 1 horizontal stiffener is usual to place at 2/5th of the depth of neutral axis from the compression flange).

Vertical +2 horizontal stiffeners are provided if the web is less than d/250 (in this case this 2nd horizontal stiffener is usually placed at neutral axis).
(1)

Pankaj chaudhary said:   8 years ago
A is correct.

No stiffeners are provided if web is less than d/85.

Vertical stiffeners are provided if web is more than d/85 but less than d/200.

Vertical +1horizontal stiffeners are provided if web is more than d/200 but less than d/250 (in this case this 1 horizontal stiffener is usuall place at 2/5th of the depth of neutral axis from the compression flange).

Vertical +2 horizontal stiffeners are provided if web is more than d/250 (in this case this 2nd horizontal stiffener is usuall place at neutral axis).

PARTHA said:   6 years ago
The answer is fine if you consider the following case as vertical stiffened web plate.

Here min web thickness is concerned so d/250 is the correct answer.

Vertical +1horizontal stiffeners are provided if the web is more than d/200 but less than d/250 (in this case this 1 horizontal stiffener is usual to place at 2/5th of the depth of neutral axis from the compression flange).

Pankaj said:   4 years ago
If the denominator factor is big, the thickness will be small. So if the denominator increases up to 200 thickness decreases to a minimum.

So, answer B. If vertically stiffened assumed. But I think it takes 250 because it hasn't differentiated between horizontal and vertical stiffener.

Sona college said:   4 years ago
D is the correct answer. Because. They asking only about vertical stiffner they didn't mention whether there is need of hzt stiffner or not.

So, We can take a minimum value.

D/t=250.
T= D * 0.004.

Satyamev said:   7 years ago
Minimum D/200 max is D/85.

If the thickness exceeds d/85 then no stiffener required because. There is enough strength to carry the load as the thickness is more.

So, the minimum d/200.

Prasad gund said:   4 years ago
According to me , when the d/t is less than 85 then vertically stiffened are not provided but if the value is in between 85 -200 vertically stiffened are provided so the ans is A

Deepak said:   8 years ago
According to the question, The answer will be min. 85 and max 200 for vertical stiffness. So I think answer A is correct.

Ganesh said:   10 years ago
d/t<85 no stiffener.

d/t 85-200 vertical stiffener.

d/t 200-250 vertical stiffener and 1 horizontal stiffener.
(1)

Sunil bhandekar said:   3 years ago
According to IS 800-1994,
Vertical stiffened d/200 should not less than but according to IS 800-71 it's d/250.
(1)