Civil Engineering - RCC Structures Design - Discussion

Discussion Forum : RCC Structures Design - Section 4 (Q.No. 37)
37.
The maximum ratio of span to depth of a slab simply supported and spanning in one direction, is
35
25
30
20
15
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
18 comments Page 1 of 2.

Prasad said:   5 years ago
The above answer is right.

But as per cl 24.1, cl 23. 2.1 IS456 2000,

Basic values of~span to effective depth ratios for spans up to 10 m.
Cantilever 7.
Simply supported 20.
Continuous 26.
For spans above 10 m, the values in (a) may be multiplied by lo/span in meters, except for cantilever in which case deflection calculations should be made.

For two-way slabs of short spans (up to 3. 5 m) with mild steel reinforcement, the span to overall depth ratios given below may generally be assumed to satisfy vertical deflection limits for loading class up to 3 kN/m.

Simply supported slabs 35.

Continuous slabs 40.
For high strength deformed bars of grade Fe 415. The values given above should be multiplied by 0.8.

Amar said:   7 years ago
Above answer is right.

But as per cl 24.1, cl 23. 2.1 IS456 2000,

Basic values of~span to effective depth ratios for spans up to 10 m.
Cantilever 7.
Simply supported 20.
Continuous 26.
For spans above 10 m, the values in (a) may be.

Multiplied by lo/span in metres, except for cantilever in which case deflection calculations should be made.

For two-way slabs of short spans (up to 3. 5 m) with mild steel reinforcement, the span to overall depth ratios given below may generally be assumed to satisfy vertical deflection limits for loading class up to 3 kN/m.

Simply supported slabs 35.

Continuous slabs 40.

For high strength deformed bars of grade Fe 415. The values given above should be multiplied by 0.8.

Amar said:   7 years ago
Above answer is right.

But as per cl 24.1, cl 23. 2.1 IS456 2000,

Basic values of~span to effective depth ratios for spans up to 10 m.
Cantilever 7.
Simply supported 20.
Continuous 26.
For spans above 10 m, the values in (a) may be.

Multiplied by lo/span in metres, except for cantilever in which case deflection calculations should be made.

For two-way slabs of short spans (up to 3. 5 m) with mild steel reinforcement, the span to overall depth ratios given below may generally be assumed to satisfy vertical deflection limits for loading class up to 3 kN/m.

Simply supported slabs 35.

Continuous slabs 40.

For high strength deformed bars of grade Fe 415. The values given above should be multiplied by 0.8.

SK ABDUL SURAJ said:   8 years ago
Simply supported and spanning in one direction 30.
Continuous and spanning in one direction 35.
Simply supported and spanning in two directions 35.
Continuous and spanning in two directions 40.
Cantilever slabs 12.

Vipin said:   1 decade ago
How it is possible, it should be 20 (option D)?

As per I.S 456:2000, L/D ration is mentioned below.

For Cantilever Beam - 7, Simply supported Beam - 20, Continuous Beam - 26.

VIJILESH T K said:   4 years ago
@Amar @Prasad.

How did you say the answer is correct by pointing to the IS 456 Provision?

Where is 30 in it? Please explain clearly.

Rajendra prasad jat said:   8 years ago
As per I.S 456:2000, L/D ration is mentioned below.

For Cantilever Beam - 7, Simply supported Beam - 20, Continuous Beam - 26.

Syed Adnan Aqib said:   4 years ago
Well, it depends on the grade of steel being used.

Here, it seems valid for low grade upto 300MPa yield steel.

LAXMIKANTH said:   5 years ago
Normal ratio:
Cantilever 7.
SS beam 20.
Continuous 26.

Max ratio:
Cantilever 12.
SS beam 30.
Continuous 35.
(4)

Adi said:   9 years ago
@Vipin.

That is for 2 way spanning slab, for 1way it is 30 and for 1way spanning continuous slab it is 35.


Post your comments here: