The pitch of the main bars in a simply supported slab, should not exceed its effective depth by
three times
four times
five times
six times
seven times.
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
29 comments Page 3 of 3.

Bhoopender chauhan said:   8 years ago
Main bar- 3d or 300.
Dist bar- 5d or 450.
Is 456.

Navjot said:   8 years ago
It is Acc To Clauses no. 26.3.3.

Pankaj chaudhary said:   8 years ago
According to me, A should be the right answer.

BHASKAR MANNA said:   8 years ago
Can you please tell the clause no? @Sanjib.

Nayan said:   8 years ago
3 times in main bars or 600mm - whichever is smaller.

5 times in transverse or distribution or 600mm whichever is smaller.

Sanjib Chowdhury said:   8 years ago
The horizontal distance between parallel main reinforcement bars shall not be more than three
times the effective depth of solid slab or 300 mm whichever is smaller IS-456.

Chhatta bogati said:   9 years ago
Main bars 3 and distribution bar 5.

Baloch said:   9 years ago
Spacing main bars = 3 times the depth.

Transverse bars = 5 times (according to RS Khurmi).

Abhijit choudhury said:   1 decade ago
3 times the efficient depth but not more than 600 mm in case of main bars. But in case of distribution bars 6 times the efficient depth.