Civil Engineering - Building Construction - Discussion

Discussion Forum : Building Construction - Section 3 (Q.No. 21)
21.
Two columns 50 cm x 50 cm and 60 cm x 60 cm carry 80 tonnes and 120 tonnes of loads respectively. The centre to centre distance between columns is 5.00 metres. The permissible bearing capacity of the soil is 20 t/m2. If the footing is not to project more than 25 cm beyond the outside of the smaller column, pick up the correct design parameters of the footing from the following:
distance of C.G. of the loads from the smaller column = 3.00 m
the length of the foundation slab = 7.00 m
area of footing slab = 11.00 m2
width of the footing = 1.57 m.
all the above.
Answer: Option
Explanation:
No answer description is available. Let's discuss.
Discussion:
10 comments Page 1 of 1.

Gerome said:   8 years ago
Total load = (120+80)*1.1=220t.

Area of footing = 220/20 = 11 sq.m.
Dist. Of CG from the center of the small column = 120(5)/(120+80).
= 3m.
Length of the footing = (3+0.25+0.25) * 2 = 7m.
Width of the footing = 11/7 = 1.57m.
(5)

Gerome said:   8 years ago
Please explain how to get the CG and the length of the footing?

Sujit said:   8 years ago
Total load = 200 t,
self wt of f/n = 10% of total load,
And the required area of f/n = 220/20 =11 m^2.

Nikhil Parbat said:   8 years ago
The Weight of footing 10% of total load =W'.

Area of footing =(W1+W2+W')/q.
q is safe bearing capacity.
The distance of CG from the centre of the small column = (W2.l)/(W1+W).
l is centre to centre distance between columns.
* centre of gravity of footing area shall coincide with c.g of the combined load in the combined footing.
(2)

Raj said:   8 years ago
Please explain with detail steps and formula.

Ashok Dhiman said:   9 years ago
Can anyone explain it the formulas?

Swapnil said:   1 decade ago
Illustrate this problem in easy language to understand. Please.

Monalisha said:   1 decade ago
Please mention the formula so that we can understand the problem properly.

Amrin said:   1 decade ago
I can't understand this problem can you explain clearly?

Kumar Vikram said:   1 decade ago
Distance Of C.G of the 500 mm column = 1500*5/(1000+1500) = 7500/2500 = 3m,

Length of the foundation slab = 2(3.0+.25+.25) = 7.0.

Total Load = 1500+1000+Wt.of Footing(aSSUME=300 KN) = 2800KN.

Area Of Footing Slab = 2800/250(Total load / Bearing Capacity) = 11.20m^2.

Width of the Slab = 11.20/7.0 = 1.60m.

Post your comments here:

Your comments will be displayed after verification.